Question about Vmax RMS
Last Post 27 Sep 2010 08:43 AM by Tony Hodges. 1 Replies.
Please login to post a reply.
Author Messages Resolved
Eric Sandeen
New Member
New Member
Posts:2

--
24 Sep 2010 08:13 AM
I'm using a pair of CR8410-1000 CTs to monitor a circuit in a distribution panel, which will not exceed 15A (15A breakers)
Therefore these 20A Ir CTs seemed to be the right choice.

I wish to measure their output via an ADC which has an input range of 0-5V, and therefore I've biased the input by 2.5V.

I notice, however, that the CR8410-1000 CTs have a Vmax of 2.1Vrms, and the datasheet suggests that the burden resistor should be chosen to limit V across it such that V < Vl < Vmax.

In other words, the Vrms across my burden resistor will be quite a bit smaller than the ADC's range, thus reducing my measurement resolution.

What's the right solution here, should I choose something like the 50A CR8449-1000 with a higher Vmax? What happens if a larger burden resistor is used with the CR8410, does it just go nonlinear in the output, burn up, or what? :)

Thanks,
-Eric
Tony Hodges
CRM Staff
New Member
New Member
Posts:87

--
27 Sep 2010 08:43 AM
Dear Sir,

Thank you for your interest in our product lines. The correct current transformer for your application is our CR8448-2000.